This could be due to a few things, air locks, blocked or restricted pipework, system out of balance or faulty valves. Try the following: 1) Close all radiators Thermostatic Radiator Valves (TRV’s) except on one of the problem radiators. If the radiator then gets hot this will rule out a problem with the valves or a blockage. Repeat with the other problem radiators. 2) If the radiators worked then it is either an air lock which is moving around the system or it is a problem with balancing. If it is an air lock with a little persistence you should be able to eventually clear it by bleeding the radiators. If this does not work it might be necessary to drain and refill the system. If this is not successful then it is most likely a balancing problem which could include an undersized pump. You need to have the system balanced. 3) If the radiators did not work then it could be a blockage, faulty valve or an air lock. Out of these it is more likely to be an air lock which is not moving. You will need to have the system drained and carefully refilled. If this fails to resolve the problem then further investigation will be required.